Re: Lightning and neutral grounding



Roy,

You have it connected correctly.  You described it correctly.

What destroys things in a lightning strike is voltage potential.  The amount
of actual current in a strike is not as great as one would think.  I forget
what Polyphaser says a typical strike current is, but it is less than you
would think.

You have a lot of electon charge energy though that needs to be dissipated
in a very short period of time.  The earth is not an immediate ground sink,
but rather acts as a lossy capacitor.  This means that there is a finite
amount of time involved to dissipate the strike energy.  The earth can only
handle so much charge at a given time.  This is why you connect your tower
to ground over a ground network of typically 3 ground rods space 16 feet
apart on each leg.  This effectively allows the earth to absorb the charge
more quickly as you are spreading the energy over a larger area.  Perhaps
that is not 100% technically correct, but it gets the point across.

Now, when you tie all your grounds together (never mind the neutral here),
you are ensuring that all your grounds rise and fall at the same potential.
If you don't do this, the strike energy at your tower, could cause the
ground at the tower to possibly raise by several hundred volts potential
above the ground at the service entrance.  The shortest path to that lower
potential then may just be right through your house and radio.  But with all
grounds connected, then everything rises together when the strike occurs and
there is no potential difference between grounds.

If you have a properly engineered system of protection with proper grounding
and surge suppression there is no need to disconnect anything.  Commercial
radio sites on very large towers stay on the air all the time and get hit
all the time.  I'm quite sure that our local TV antennas on the Sears Tower
in Chicago get hit all the time as it's the tallest thing around here for
miles.  Yet, the stations (FM and TV) stay on the air through all the
storms.  They have proper protection and that's on top of a 1200 foot
building.

You mention rotor cables.  That's another good point that people tend to
forget.  The rotor lines can also carry strike energy and so it's
recommended to have a surge suppressor in your rotor wires as well.

If you chose to disconnect like you say, then that's your choice.  I've
heard that it doesn't necessarily protect.  And what about the time you
forget to disconnect everything and go away for the weekend and a big storm
comes by?

73,

Jon
NA9D


on 3/11/03 10:18 PM, Roy Welch at rdwelch@swbell.net wrote:

> If the Neutral line goes to ground at the Service entrance and the house
> ground wires do also then they are common at the service entrance.  The
> ground wire then comes back through the house wiring to the ground terminal
> on the 3 conductor power lead cord to the radio.  The ground lead goes to
> the chassis inside the radio as a safety ground.  The RF ground terminal on
> the radio as well as the coax shield (via the antenna) both go to the
> outside ground rod by the station.  A number 4 wire runs from that ground
> rod to the TV antenna ground rod and on around to the service entrance
> ground rod.  It seems to me that the service entrance grounded neutral and
> the safety ground in the house wiring are tied together and fan out from
> the service entrance.  However there is another path from the house ground
> wire back to the service entrance, going via the radio chassis to the RF
> ground rod and back via the three strapped ground rods to the service
> entrance neutral.  This has always bothered me, especially now that I hear
> thunder in the west :-)  I disconnect all coax leads at my coax patch
> panel, open the power at the desk fused box, unplug all rotor cables, the
> KCT to PC cable and power down all PCs when I hear thunder approaching.  I
> have a whole house surge surpressor in the service entrance box on the
> house side of the circuit breakers.  I respect that stuff.

-------------------------------------
Jon Ogden
NA9D (ex: KE9NA)

Citizen of the People's Democratic Republik of Illinois

Life Member: ARRL, NRA
Member:  AMSAT, DXCC

http://www.qsl.net/na9d   <- Updated on 1/22/03!!!

"A life lived in fear is a life half lived."


----
Sent via amsat-bb@amsat.org. Opinions expressed are those of the author.
Not an AMSAT member? Join now to support the amateur satellite program!
To unsubscribe, send "unsubscribe amsat-bb" to Majordomo@amsat.org



AMSAT Top AMSAT Home